Old 07-19-2008, 01:53 AM   #1 (permalink)
Registered User
 
Join Date: Jun 2008
Posts: 31
OS: xp


12,000 btu window unit

i have an a/c that is a 110 and mostly everytime it trips the breaker (20amps) when the compressor turns on . i have allready left the unit with its own plug . any suggetions
buenf is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!Bookmark on Thread SoupReddit!
Reply With Quote
Old 07-19-2008, 05:35 PM   #2 (permalink)
TSF Enthusiast
 
Wozer's Avatar
 
Join Date: Oct 2004
Posts: 1,010
OS: 2kpro/XP pro/MCE


Re: 12,000 btu window unit

the fact that it is on its own plug means nothing....unless by some very small chance that plug is the only one connected to the breaker...when I had my house built 7 years ago I had one plug installed with a dedicated breaker for recording use...and I paid extra for that...

the point is that its what is connected to the other plugs on the breaker that most likely matters....or perhaps the breaker is starting to go...I did a quick Google search for ac units with the specs you vaguely list and it appears as if they all fall within the ratings of a 20 amp breaker...but know this, the biggest draw that unit will give is just when it starts up, and the load it pulls may be towards the limits of the breaker just by itself...if you have another high amperage piece drawing electricity at the same time, then that is most likely the real cause...next time it throws a breaker figure out by deduction what other items are also on that circuit and deduce what item is also drawing a lot of amps....
__________________
Beware of the big 3 insurance companies in Texas! Read your policies carefully (maybe you'll need a lawyer) and enjoy the 6% increase in your rates you are about to receive from Allstate, Farmers & State Farm for most likely reduced coverage
Wozer is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!Bookmark on Thread SoupReddit!
Reply With Quote
Old 08-05-2008, 08:20 PM   #3 (permalink)
TSF Articles Team
 
mack1's Avatar
 
Join Date: Nov 2007
Location: Texarkana, Texas
Posts: 725
OS: xp sp2

My System

Re: 12,000 btu window unit

Hi buenf,

Wozer's advice is good. Wall plugs are usually connected with several on the same feed (breaker). Number 12 wire is used to wire 110 volt circuits and it is rated for 20 amperes. Do NOT entertain the idea of using a larger breaker. Breakers are rated for the wire, so that the wires won't overheat and cause a fire.

A loose feed wire connection in the wall plug can cause the a heavy load to throw a breaker. Feel of the wall plug cover and see if it feels hot when it throws the breaker. If so, it is an indicator that the wire to the plug is loose.

If you turn off the airconditioner and then immediately turn it back on, it will throw the breaker. It will still have pressure on the high side of the pump that has to be overcome at start, thus causing overcurrent. If you turn it off, wait about 30 seconds before turning it back on.

For test purposes, you could try using another circuit (in another room) using a long extension cord. A 12 guage would be best, but you might get it to work with a 14 guage. (larger number is smaller wire) Borrow one from a neighbor or friend if you don't have one.

The problem could also be the Start Capacitor in the unit. It is used to shift the phase of the current during start for heavy load. After start, a run capactor is switched in for best run phase shift characteristics. If you changed out the capacitor yourself, it would be $10 or less. Cost a lot more if you had someone to do it.

If you find that the unit kicks out other breakers using the extension cord, it is probably a start problem in the unit. One ton units are't that expensive, so it might be time to replace it unless your like the idea of replacing the run capacitor.

Hope this helps,
Mack1
__________________
"If you like yourself others will like you also" me
"Don't drink downstream from the herd" Will Rogers



mack1 is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!Bookmark on Thread SoupReddit!
Reply With Quote
Reply


Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



All times are GMT -7. The time now is 10:17 PM.



Copyright 2001 - 2008, Tech Support Forum

Search Engine Friendly URLs by vBSEO

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81